6500 watt diesil generator /as soon as i put any

6500 watt diesil generator /as soon as i put any load on it shuts down even with one light if i flip the breaker it will shut off / i replaced all the electronics, generator itself from another that was workin but blew an oil seal

1 Answer

sal sabea

Level 2:

An expert who has achieved level 2 by getting 100 points

MVP:

An expert that got 5 achievements.

Governor:

An expert whose answer got voted for 20 times.

Hot-Shot:

An expert who has answered 20 questions.

  • Expert 98 Answers
  • Posted on Oct 26, 2009
sal sabea
Expert
Level 2:

An expert who has achieved level 2 by getting 100 points

MVP:

An expert that got 5 achievements.

Governor:

An expert whose answer got voted for 20 times.

Hot-Shot:

An expert who has answered 20 questions.

Joined: Oct 11, 2009
Answers
98
Questions
0
Helped
50517
Points
203

If by fliping the breaker it shuts off..that means there is a short circuiting in the breaker..try connecting your house,shop..etc..directly ...
that is if the shut off reason is overloading...if not please explaing with details

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1helpful
1answer

Capabilities of the Robin 2400is generator

no
ac units are 2000 watts minimum, washing machines are 1500 watts minimum, microwave is what is on the plate and start at 650 watts but most are 2000 watts
the 2400 is the peak out put for start up of fridge , washer etc and the running wattage will be 2000 watts or less ( duty cycle )
to run more than one of the nominated items at once you will be needing a 5500 to-6500 watts unit
they handle a start up surge of 6500 watts ( larger one) and will comfortably handle 5500 watts run full load
it works like this , the plate on the gen set is the surge short time load capacity of the genset and not the duty load which is 500 to 750 watts less than that plate wattage
for example your 2400 is is surge rated at 2400 watts but duty load is less than the 2000 watts
many people make the mistake of buying a gen set that looks big enough but do not calculate the maximum load capable on being put on the gen set
fully loaded uses more fuel /hr
wears out faster
has power surges as the extra load cuts in and the motor struggles to get back to required rpms for voltage and cycles
will not cover extras like lights ,
a much large gen set will take it all in it's stride , no power surges, better economy, less stress
talk with an electrician , do your maths on everything you wish to run and that which you forgot about then add 1000 watts to the duty cycle and that will be close to the gen set you require
0helpful
1answer

On my 9 hp onan genset it runs fine but the 20 amp breaker on makes it shut down is there short or abad breaker

To determine if it is from the breaker use a

Tong Tester


These would indicate what current is being consumed by the load.
0helpful
1answer

Just paid over 1,500 last year an has not rungood since. starts up real good, but once aair is turned on it stops running, or it might run one air at times. on my way back to michigan an not a happy...

This generator is a 5KW model. This means it can supply up to 5000 watts of power, total. Not all devices list the watts they need to be provided - instead these devices list the power they need as volts and amps. This can make it hard to determine what the actual watt requirements are for the device.

Overly simplified, watts is equal volts times amps (watts = volts x amps). A single 120 volt light bulb that uses .833 amps consumes 100 watts. If you checked a regular 100 watt light bulb with an ammeter, you'd find it does indeed draw .833 amps.

Working the formula a different way, we can learn how many amps this 5000 watt generator can supply at 120 volts, too. If all the loads you need to connect to this generator are 120 volt types, that means the total amount of amps the generator can supply is 5000 watts / 120 volts = 41 amps purely resistive loads (like a toaster or light bulb) maximum under ideal conditions. There is never a time when ideal actually happens, and not all loads are purely resistive - many are inductive. Inductive loads are motors (like your A/C), fluorescent lamps, computer power supplies, etc. - so figure more like around 30 amps total instead.

If you try to connect devices that require more than 30 - 35 amps, the generator will probably have problems trying to supply this load for any longer that a short length of time. Additionally, motors like those in A/C compressors draw significantly more power when first starting and can cause the problem you are describing. Try running the generator with loads other then the A/C to see how well it can supply the load(s). Or try running only 1 A/C unit and other non-A/C loads.

What I'm trying to tell you is that you may need to do some active load management to be sure that you aren't trying to get more power out of the generator than it is capable of supplying. You may need additional generators or swap this one to a larger size to handle the load properly and safely.

I hope this helps & good luck!
0helpful
2answers

Onan Portable Generator - 5000 , Model# 6500: I have china generator capacity is 2700 watts but ...

Alternately,



• Turn-off all lights first.

Run your pump or water start motor.



• When the motor is running,

Turn on the lights , one at a time.
0helpful
1answer

Cannot get generator to shut down, please

run a wire from the plug to theframe and put a switch inline and that way when you turn the switch on it will ground out the plug
0helpful
1answer

Yamaha 6500 watt diesel runs but usually shuts

First thing to monitor is the fuel solenoid power. See if it is the thing that goess away to cause shutdown.

Tracing this back there is only a few things that control this: The battery, the low oil shutdown switch, and the run switch, and associated wiring.

If I were to ventture a guess, I would put money on the low oil shutdown switch.
0helpful
1answer

6.5 RV Onan generaotr wont kick in when loaded. checked automatic transfer switch and excited it manually, worked one time but never again,

1. Does the generator stay running when you start it the first time?

2. What color is the housing on this generator? Try to get the model number and serial number.

If the genset is shutting down on the first try, then your probably not creating voltage. However, if this is an older unit then the genset may stay running although no voltage is created. Place a volt meter on the genset to check for output voltage.
Not finding what you are looking for?

197 views

Ask a Question

Usually answered in minutes!

Top Electrical Supplies Experts

Brad Brown

Level 3 Expert

19187 Answers

ADMIN Andrew
ADMIN Andrew

Level 3 Expert

66973 Answers

CJ Rock
CJ Rock

Level 3 Expert

4429 Answers

Are you an Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...