Robert Brenner Posted on Dec 19, 2014
Answered by a Fixya Expert

Trustworthy Expert Solutions

At Fixya.com, our trusted experts are meticulously vetted and possess extensive experience in their respective fields. Backed by a community of knowledgeable professionals, our platform ensures that the solutions provided are thoroughly researched and validated.

View Our Top Experts

Trying to driveRHEEM RAMB-036JAZ using a Honda eu2000 generator. How to hook this up?

Trying to keep gas heat going when electrical grid goes down. Simply plugging furnace power plug into extension cord and then into the Honda eu2000 does drive the furnace fan once the heat box reaches set temp.

1 Answer

Happy Valley Air Care LLC

Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Novelist:

An expert who has written 50 answers of more than 400 characters.

  • Expert 199 Answers
  • Posted on Dec 20, 2014
Happy Valley Air Care LLC
Expert
Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Novelist:

An expert who has written 50 answers of more than 400 characters.

Joined: Dec 24, 2012
Answers
199
Questions
0
Helped
61903
Points
316

You have to very careful powering up home appliances on portable generators due to back feed problems to incoming lines. I would recommend getting an experienced electrician to show and explain the problems with what you are considering. Many linemen have been shocked due to backfeed. The real way to perform this is to get the controller that is put on home generating systems such as generac type systems. These automatically isolate line supply from backup power from home generators, thereby eliminating shock hazards to linemen.
If prolonged shortage, you could disconnect the wires into the furnace and install an extension cord from the furnace to the 120 volt plug on the generator. Most fans are powered on gas furnace on 120 volt. Make sure your voltage needed on your furnace before attempting emergency power up. I have seen some furnaces power by 240 volt fan motors. If it is 240 volt then use the 240 plug wired correctly. PS when you get an electrician to help you with the wiring, check out the requirement to provide grounding, to lessen your shock hazard.
Hope this helps.

5 Related Answers

Anonymous

  • 1420 Answers
  • Posted on Nov 20, 2007

SOURCE: Honeywell Gas Furnace

A Make and Model number of the furnace not the thermostat will help but I can walk you thru the operation of a typical furnace. It sounds to me that the burners are igniting properly but the flame sensor is not sensing the flame and shutting down the system. You will need to find the sensor and clean it and check the wire from it to the control board. Typically, the flame sensor is found at one side or the other of the burner box. It is a small probe that the flame hits. Depending upon your model it may have a small wire attached to it leading back to the control. Or it may be part of your auto-pilot assembly. ? At any rate, you will need to get to it and very delicately brush it off. Then inspect the flame channel. This is a trough area where the flame travels to ignite all burners. Over time, they tend to fill with rust and debris. Take a small screwdriver and run the blade down the trough. Inspect the wire that goes from the flame sensor to the control board. Make sure it is not frayed or broken or shorting out and that the connection at the board is good.

Beyond that, it's time for a technician to come.

Let us know the Make and Model of the furnace (found inside the furnace cabinet) and maybe we can help you further.

Ad

Ken Bledsoe

  • 306 Answers
  • Posted on Dec 21, 2008

SOURCE: Furnace doesn't reach desired temperature

One of two things you can try. Do you own a volt ohm meter? Anytime your unit cycles short like it is doing the control circuit which on this one is 24 volts that engages relays and controls the gas valve to open and close. I am thinking the heat exchanger is getting so hot it is tripping the upper limit which for the most part is around 180 degrees. So next time it turns off take your ohm meter and with the power to the whole unit off. Either turn the breaker off or there is a light switch that is real close to unit turn it off. Undo the two wires to the gas valve and ohm them out. You should have continuity if you get nothing check each limit switch should have a couple. Undo wires to them and check. If you find one that is open more then likely the upper one. They are a safety device that keeps the unit from getting too hot.

There might be another option increase the speed of your fan motor to get the heat out of furnace quicker. Look at the circuit board notice the fan wiring going to it. The Red wire from fan is low speed look to see if it is on HEAT on the board. You should have 4 speeds to pick from you could take the black off of COOL and swap wires and test the unit by doing that. I'm going to put a solution on this so I can come back to it quicker. Even though we a just testing it for now. ken

David Metcalf

  • 3 Answers
  • Posted on Mar 07, 2009

SOURCE: Ruud Electric Furnace Cannot Reach Setpoint - "Watt Restrictor"?

unfamiliar with watt restrictors.
heat strips have 2 safety devices, a thermal overload, they get to hot they shut off, cause not enough air flow increase fan speed this device is auto reset. a fusible link a fail safe to thermal over load, no reset and sometimes replaceable. if this does not help would like to ask you a few questions. one of the buildings i take care of has 200 + reem/ ruuds all electric heat. if a part is defective replace, please do not by pass. safety frist.

bobicehouse

Robert Moller

  • 1524 Answers
  • Posted on Apr 23, 2009

SOURCE: Intertherm model MGHA-090-AAPQ -- combustion air keeps running

Sounds like a problem with the circuit board.

Anonymous

  • 106 Answers
  • Posted on Jun 04, 2009

SOURCE: rv electrical question

By the main breaker in the camper, do you mean the main 24 or 12 volt breaker, or the incoming 120vac breaker? Is it tripping the breaker in the camper, or the house? If it is tripping the breaker inside, i would look for maybe water damage, rusty components, maybe have an electrician come look at it, not worth going out away from home, and that problem ruining your vacation! Does this unit have a generator set? Try disconnecting the generator too. Hope that helps!

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1helpful
1answer

Ex1000 honda generator getting no gas to sparkplug. new plug,, dry when taken out after trying to start. generator has sat for 1+ year

Carburetor, injectors likely gummed up. It is a common problem. Try spraying carburetor cleaner into the intake and get it to run briefly by burning the cleaner. Keep trying that until you get it to run.
0helpful
1answer

Greetings. I have a eu2000 honda inverter with the following problem. The high generator runs too fast, when the idle is activated, slows down a bit, but does not increase

on the governor control back to the carby , there is a screw that adjusts the spring tension for the governor arm
that screw is the adjustment for engine operating rpm not the idle screw
0helpful
3answers

How to find portable generator brands?

There are numerous sites online that are providing specifics of portable generator. These are typically specially manufactured for those people who are looking for good quality portable electrical generator and it's assessment. To find out more please click here.
Best Selling 2000 Watt Portable Generator Brands 2016 Top Brands Guide
0helpful
1answer

Should i use regular gasoline in 2000 watt generator

It is ok to use 87 octane regular unleaded gasoline in a Honda EU2000 generator. I have been running it in mine for 4 years with no problems. Using the higher octane blends is just a waste of cash.
0helpful
1answer
3helpful
1answer

I am trying to determine the specs on my Rheem Criterion II lx2000 heating/AC unit unit installed in Sept 99, I blieve it was manufactured 2/5/99 based on AC Pump serial number 6263F259928697 Model RAMB...

rheems site is secure for dealers only but i can tell you. its a 3 ton unit 12 SEER R22 unit. The coil (rcga) is a 3 ton coil The AC is a 1999 and coil 1998. the # you have for the heater is accually just the honeywell gas valve. the model for the heater would be on the inside wall near the gas valve.
0helpful
1answer

Honda eu2000 generator starts but no power to panel

You probably need to do a tune up. Change the spark plug, oil, air filter, and you may also need to add new fuel.
Not finding what you are looking for?

124 views

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...