Kohler 12 kW Emergency Power System - 12RES-L - Answered Questions & Fixed issues

0helpful
3answers

I have a new Kohler 12kw res generator on propane - backfiring

Is the outside air temp cold. These generators will backfire if it is real cold and if the propane pressure is low. It is suppose to be 11 to 12 inches of water colume at the generator fuel input. drygwals
6/8/2023 7:22:42 AM • Kohler 12 kW... • Answered on Jun 08, 2023 • 1,770 views
0helpful
3answers

I have a Kohler 12RESM1 propane generator with oc/uu code

U need to make sure that the relay driving ur auto start stay closed all thru the crank cycle.
1/16/2021 9:20:36 PM • Kohler 12 kW... • Answered on Jan 16, 2021 • 2,917 views
0helpful
2answers

How can I reset the "programmed exercise mode" on my Kohler 12 RES generator

You will likely need to reference your instruction manual for that specific control panel.
9/24/2017 2:18:45 AM • Kohler 12 kW... • Answered on Sep 24, 2017 • 2,065 views
0helpful
3answers

Starter battery will not charge

Hi
If the starter battery is not taking a charge, then it may have failed and require replacement. It is not uncommon for a battery that sits on standby for long periods of time to eventual fail. Best approach is to contact Kohler direct or one of their service agencies to get the correct replacement battery for the generator system.
You can contact them here
regards robotek
7/26/2015 10:31:28 PM • Kohler 12 kW... • Answered on Jul 26, 2015 • 490 views
0helpful
1answer

MY YAMAHA 6600DE GENERATOR STARTS AND DIES WHAT COULD BE THE PROBLEM

this sure sounds as if the low oil cutoff is activating for some reason , look at switch carefully to see any physical dammage (ck oil level as well)
1/30/2015 3:26:11 AM • Kohler 12 kW... • Answered on Jan 30, 2015 • 263 views
0helpful
1answer

My kohler 12res starts but governor moves constantly which makes my voltage erratic

this is a common complaint to these , what it boils down to is allways a fuel problem , if its gasolene then its in the carb if it's nat gas then it's in the regulator/vaporizer you'll have to clean these items to see if that helps . someof those liguid cleaners sometimes works but i find a good dissassembly cleaning to be the best
1/30/2015 2:20:43 AM • Kohler 12 kW... • Answered on Jan 30, 2015 • 240 views
0helpful
2answers

The starter on the 12res Kohler generator just hums (spinning sound). It doesn't engage the flywheel. Do I need a new starter?

OC is over crank failed to start. It will normally try 3 times before giving this error. You need to disconnect the battery and remove the starter motor, make sure it is free to move / spin. Either the starter has seized or the engine has siezed. Make sure the engine is free to rotate also, once you remove the starter you will see the engine flywheel there, removing the spark plugs will make it easier to rotate the engine. I would guess it is more the starter.
11/8/2014 10:31:47 PM • Kohler 12 kW... • Answered on Nov 08, 2014 • 949 views
0helpful
2answers

Overcrank error message

The 'overcrank' error simply means it tried to start but never actually started. It cranked for an extended period. Check the fuel and starting issues you would normally check to start the engine. If you need further help, I’m available over the phone at https://www.6ya.com/expert/craig_3fa289bf857b1a3c
6/11/2020 12:25:24 AM • Kohler 12 kW... • Answered on Jun 11, 2020 • 12,628 views
0helpful
2answers

Have Kohler 12RES. Gives a CC1 code thenan OC

check your load wires there probaly reversed. I had the same problem friday. The week before the electrican wired it. did the same cc1 then oc. had a generator company come out it was the wireing. my load and netural were reversed.
12/22/2013 12:25:36 AM • Kohler 12 kW... • Answered on Dec 22, 2013 • 5,426 views
0helpful
1answer

Kohler 30RES

Sorry I meant low coolant sensor, not low oil
12/1/2013 10:55:14 PM • Kohler 12 kW... • Answered on Dec 01, 2013 • 316 views
0helpful
1answer

Kohler 30RES Generator LOC code coolants ok

How old is the 30RES? unplug the low oil sensor on the radiator and see if it runs, they are notorious for failure and have to be filled in the radiator to the brim. If it runs order a new sensor, I have replaced many of them for this reason, but more often the radiator seems full by dipping finger in, but will always take more coolant. The sensor is mounted so high up in the radiator. I ask the age as newer ones require a signal to be maintained and it isn't just a simple ground if low on coolant, if it has 3 wires then disconnecting for the above test will not work
12/1/2013 10:54:56 PM • Kohler 12 kW... • Answered on Dec 01, 2013 • 740 views
0helpful
1answer

Kohler 7.3e marine generator exhaust is coming out of valve covers. It's not blow by and I've check the valves are not sticking and gaped properly.

Valve seats, valve integrity, intake seals. Perform a leakdown test to further diagnose
3/3/2015 3:29:15 AM • Kohler 12 kW... • Answered on Mar 03, 2015 • 554 views
0helpful
1answer

How to reset FAIL TO START(over crank)?

Over crank is just that too much cranking with a filed to start. Plese check gas pressure and for voltage on the fuel shut off solenoid
11/27/2013 1:06:38 AM • Kohler 12 kW... • Answered on Nov 27, 2013 • 1,641 views
0helpful
1answer

Problem with kohler 12 kw, showing 38 . 1 code

Normally fault codes are letters? I am not familiar with that code at all. You may have got the control in some configuration setup code 3P0(X) is for raising and lowering the voltage where X is a number from 1-9 for increase
11/22/2013 3:45:56 PM • Kohler 12 kW... • Answered on Nov 22, 2013 • 186 views
0helpful
1answer

I have a 12RES showing 114 volts on phase and 124 volts on phase 2. 240 v between phases. Is this typical?

No it is not typical, you never indicated if you are measuring it under load or not. Repeat that test under 1/4 load and see if they even out.
11/16/2013 7:08:29 PM • Kohler 12 kW... • Answered on Nov 16, 2013 • 65 views
0helpful
1answer

No 110 ac power out of gem

Check the rotor slip rings for tarnish as it has sat.If they are clean, the rotor may have lost it's magnetism and may need flashing (putting DC power directly on it for approx 3 seconds) with brush wires disconencted POLARITY IS CRITICAL
11/16/2013 7:06:30 PM • Kohler 12 kW... • Answered on Nov 16, 2013 • 141 views
0helpful
1answer

I have kohler 12res 60hz generator can I covert to 50hz ? If yes than how can ?

No you cannot, a 60HZ unit is designed to run (and the controller expects to see 60HZ) RPMS 1800 for a 4 pole rotor and 3600RPM for a 2 pole. Slowing engine speed down to 1500RPM the controlelr would see it as under frequency
11/16/2013 7:04:44 PM • Kohler 12 kW... • Answered on Nov 16, 2013 • 140 views
0helpful
1answer

How do you check the slator to see if it is any good useing a multymeter

You must first disconnect ALL the stator wires to prevent a bad reading. You MUST have a good meter, cheap ones will not do. Put the meter on Ohms and put the probes together, note reading (this is the resisitance of the meter wires and this reading will need deductiong from the test readings). You will need a service manual to know what that actual values should be at what ambient temp. They are normally very low less than 1 ohm so cheap meters won't read. Check each wire with one lead and the other to the stator metal ground. You should have ZERO any value here is a short. Then check between each pair and read the value (many stators have multi windings T1,T2, Q1 Q2, B1 B2 etc, so you need to make sure you measure across each pair.. Generally values are 1 ohm or less
11/16/2013 7:02:22 PM • Kohler 12 kW... • Answered on Nov 16, 2013 • 135 views
0helpful
1answer

I have an older Kohler Power Pro 5000kw generator

try contacting Nixon Power Services in TN. If they cannot help, you take the old rectifier out, note wiring. A rectifier is nothing special as long as it is the same current rating, if the part is truly obsolete then a good electrnic supply house can give you an equiv
11/16/2013 6:58:05 PM • Kohler 12 kW... • Answered on Nov 16, 2013 • 217 views
0helpful
1answer

Kohler parts

Contact Nixon Power Services in TN. Make sure the controller is programmed for your model and gas etc before it is shipped
11/16/2013 6:52:42 PM • Kohler 12 kW... • Answered on Nov 16, 2013 • 91 views
Not finding what you are looking for?
Kohler 12 kW Emergency Power System - 12RES-L Logo

119 questions posted

Ask a Question

Usually answered in minutes!

Top Kohler Electrical Supplies Experts

Brad Brown

Level 3 Expert

19187 Answers

john h

Level 3 Expert

29494 Answers

ADMIN Andrew
ADMIN Andrew

Level 3 Expert

66855 Answers

Are you a Kohler Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...