20 Most Recent
Northstar Belt Driven Generator Head 5500 Watt Questions & Answers
My NorthStar 5500 generator head no longer produces any electrici
Specs do not mention a maximum safe rpm but the recommended shaft speed is 3600rpm. Even though it isn't a premium product I can't imagine the manufacturer would be so foolish as to design it so it breaks if that speed is exceeded by a reasonable amount for a short amount of time. The big question is what is a reasonable amount - I reckon a safety margin of 25% would be reasonable for a budget priced product and up to 40% for a premium product.
Over-revving is unlikely to do very much damage to the stator but the armature is at risk of damage and being brushless or self-energising, unless there is visible damage it is a difficult item to test without dedicated equipment.
I suggest you recheck all plugs, connections and cables and if no faults are found contact the manufacturer or dealer for advice, costs, etc...
Northstar diesel generator 6500 main bracker tripping at low charge
Tripping phenomenon
A.Ifdiesel gensetoperates under rated conditions for a few minutes, the automatic air switch trips, after recloses, then trips a few minutes later with a burning odor.
The cause:
The main contact of the automatic air switch is not well contacted or the spring pressure is insufficient. and the lead-out wire of the switch is not well contacted. The above two reasons will increase the contact resistance of the main circuit of the automatic air switch and cause serious fever, which will lead to the action of the thermal release and lead to wrong tripping.
Methods of resolution:
At this time, we should clean the main contacts of the automatic air switch and flatten them with a fine file or fine sandpaper; Adjust contact spring pressure to make good contact; clean contacts, apply conductive paste if necessary, and lock connection screw.
1/3/2020 3:49:43 AM •
Northstar...
Answered
on Jan 03, 2020
Generator had been running for 3 hours with a/c and refrigerator and lights (on concession trailer)when we experienced a loss
the unit has gone into over load
The total power requirement has exceed the output of the generator
for example if the generator is a 2.500 kw or kva then it will generate well at 1.8 kva or kw but it will not run forever at 2.5 kva -kw
When a ac is running the power requirement will be constant on the generator and with the fridge as well then the load will be at the maximum out put of the unit.
when the fridge starts again the extra load will exceed the max out put of the generator and it will slow down ( lights dimming ) and eventually go into overload mode
have an accredited electrician calculate your maximum load requirement for an external power supply and then get a unit that is at least 15.. kva kw better that required
generally fridges use 1000watts , ac conditions will draw over 3000watts and any thing else adds up . I am guessing that your generator is only 2500 unit
4/13/2015 6:18:49 AM •
Northstar...
Answered
on Apr 13, 2015
I have a northstar generator that runs but not putting out any power
If it has sat, it may have lost it's rotor residual magnetism. Disconnect the rotor field wires at the AVR or on the exciter/brushes. Note they are polaroty sensitive. Connect a 12V battery to F+ and F- (note polarity) and momentarilly power from the battery for a few seconds. DO NOT forget to disconnect the rotor/exciter field wires first or the voltage regulator will be damaged. If it hasn't sat check voltage regulator, rotor resistance, and stator resistance, and for shorts to ground.
3/1/2015 9:40:11 PM •
Northstar...
Answered
on Mar 01, 2015
My generator is not putting
Most low voltage conditions on generators are simply due to a low engine rpm. Most modern generators are 2- pole windings. So your engine rpm should theoretically run @ 3600 rpm. which will produce 120/240 volts @ 60 HZ. In actuality You want to set your rpm's @ Approx. 3720rpm no load. About 62.5 Hz. Without getting to technical this will give you your desired 120/240 volts loaded. Hope this helps.
8/10/2010 12:11:03 AM •
Northstar...
Answered
on Aug 10, 2010
