I have an 8KW Generac gas generator. We had a power outage and it didn't auto-start. ALARM - Overcrank msg. Started it manually. Weekly exercises are fine (It's cold and snowy here .. relevant?)
CJ Rock
Level 3:
  • Generac Master 4,429 Answers
  • Posted on Mar 18, 2019
CJ Rock
Generac Master
Level 3:
Answers
4429
Questions
0
Helped
1644589
Points
15024
By "gas" I assume you mean gasoline? Overcrank means too many starter revolutions without engine run which agrees with no auto-start.
If gasoline, suggest you drain the fuel bowl and some of the tank(pint or so). Capture fuel into container. Then transfer to a transparent/glass container and let set a few minutes. Then look for a water line(fuel is lighter than water and will separate). Line high in jar means lots of water. If any sign of water and you need to clear the fuel system and tank. Then completely fill with FRESH fuel from a trusted source. Or if refueling too far, if you only use fuel from top of container that has sat for a few minutes, the water is on bottom and fuel on top.
5 Related Answers
Anonymous
  • 169 Answers
  • Posted on Jan 26, 2009
SOURCE: Generac Guardian 15kW Generator
That sounds just about right, if the relay contacts get welded together it sometimes takes out the driver on the printed circuit board. As you found out, 12vdc from 23 to 194 makes the transfer switch move to the Generator position, relay not energized makes the ATS move to the Normal position.
You can make a nice test function by installing a 10 amp contact switch in series with either the N1 or N2 terminals. When the switch is open the generator thinks the Normal power has failed.
Regards,
Carl
Anonymous
  • 169 Answers
  • Posted on Apr 06, 2009
SOURCE: 10kw Generac shut down overspeed
Make sure that the throttle linkage is all there and not damaged/misadjusted, then get a manometer and check your inlet gas pressure. Gas pressure should be 8 inches of water column and stay there running or not.
Carl
mydogisk
Kenneth
  • 50 Answers
  • Posted on Apr 13, 2009
SOURCE: Guardian generac 10kw model 5502 does not output correct voltage
the instructions says the voltage regulator is automatic/digital. when you check the voltage is there any load on the generator? if applying load to the generator doesn't help, you can manually change the motor speed where the governor connects to the carborator, but it may change the frequency, but the regulator may fix it
Bob Janelli
  • 26 Answers
  • Posted on Oct 01, 2009
SOURCE: Generac 43903 standby Generator overspeed indicator on starting
I have a generator that did the same thing. It would start and then stop within a few seconds. The more expensive generators have an oil level safety switch to prevent the engine from burning up. There is usually a wire connecting to the switch on the outside of the engine near the oil fill hole. Remove this wire and try to start the generator. If it runs without a problem then it is the switch. You need to remove the switch and take it apart carefully and clean it. There is a small float inside the assembly. When the oil runs low the float allows the switch to short to ground which kills the spark to the spark plug. Hope that helps.
Bob Janelli
I’m happy to help further over the phone at https://www.6ya.com/expert/bob_62dfa2f81bb55288
Testimonial: "This is good information in the event that the low oil switch is part of the problem."
Anonymous
  • 10 Answers
  • Posted on Oct 12, 2009
SOURCE: I have a 17kw generac generator that will run
I have the 18KW model and was told that most alarms relate to a low battery. Make sure the battery charger in the Transfer Switch is properly feeding the battery or hook up a mobil battery charger to the battery and see if the alarm goes away. Good Luck.
1helpful
3answers
Generac Guardian Standby Generator 04760 15KW LP won't stay running
Turns out it was the Manual-off-Auto switch that was bad. My DVM showed a voltage drop across the switch. The controller wasn't getting enough power.
One good thing about it was it forced me to really study the schematics to understand how everything worked. I'm now in the process of designing my own esp32 based controller, with wifi connectivity, to replace the stock control board.
Generator hard to start and sputters like its missing
About 15,000 results (0.73 seconds) Search Results
    2 - Generac : Questions, Answers, How To, FAQs, Tips ...
    answers.generac.com/answers/1506-en_us/searchquestions.htm?...
    Can I run an 8kw standby generator on a 100 lb propane tank? 2 answers ... What am I getting for the extra cost of the Guardian unit? ... The engine starts hard and runs rough. 1. Air ... On auto start, unit sputters and I smell gas. ... Does the gas and electrical feed into the unit from the back as previous air cooled units?
    2 - Generac Questions and Answers
    answers.generac.com/answers/1506.../generac.../questions.htm?...
    On auto start, unit sputters and I smell gas. .... The 20kW automatic standby generator has the option to delay start up during an ... This is for a guardian 20kw. ....has been designed to make the battery installation and removal so difficult? ... The air cooled generators are designed to allow for the smallest footprint while still ...
    3 - Generac Questions and Answers
    Generac's Guardian Series 17kw automatic standby generator does not come with a.... The automatic response features of our air-cooled units initiates the unit's startup,.... This week I tried the same and it tries to start but just sputters and fails until .... A C delayed start still chocks 17kw generator would a hard start kit help?
    On auto start, unit sputters and I smell gas. On manual start ...
1helpful
2answers
I have a natural gas generac 8kw it was running fine now it will not run found that out after the last power outage pull the plug looks good found that it will not spark at the plug
How old is it???? Does it have a read out that tells you what's wrong?????When is the last time you did a maintaince tune up on it???? Mine is fueled by propane and I changed the oil and plugs and it's been fine since....Sometimes it's the starter/ignition..I would do a complete tuneup first, then clear codes, then try starting it up manually....If that works put it back on auto..Good Luck
How to replace battery in a generac standby 8kw generator
Switch generator to off. Remove 7.5A fuse. Disconnect Negative (-) battery terminal first and then Positive terminal (+). slide battery out the front (may be a tight fit) and install the new battery reversing removal steps. Connect (+) first and (-) last. Reinstall 7.5A fuse and switch to manual to start and test run.
3answers
Generac 20,000kW Standby generator doesn't start shows message STOP ALARM OVERCRANKED
Overcrank means that it tried to start and couldn't. It will go through 5 crank cycles and then stop with this alarm. Switch to off, hit enter to clear fault and then try to start in manual. Check to make sure you have fuel and pressure is 11 to 14 in WC.
4helpful
How do i reset overcrank alarm on my generac 0058750 generator
You turn the unit to the off position, hit enter twice on control board, and put back in manual, this should reset this fault
4helpful
2answers
Overcrank error message
The 'overcrank' error simply means it tried to start but never actually started. It cranked for an extended period. Check the fuel and starting issues you would normally check to start the engine.
If you need further help, I’m available over the phone at https://www.6ya.com/expert/craig_3fa289bf857b1a3c
4helpful
Start runs shutsdown
Typically caused by the fuel line (LP or Natural Gas) having a lot of air in it. Was your generator just installed, or was there any work done to the gas line of the building / generator? Consult local gas contractor / propane dealer / gas company for assistance in purging the fuel line.
A low battery can also cause this as well as the generator is not able to come up to starting speed quick enough. Try placing a stand alone battery charger on the generator and charge the battery. Also check the air filter as well.
OverCrank condition occurs when generator tries to start itself, or be manually started, and the starter spends too much time turning.
This can also indicate failure of the control board. This will need the expertise of generac technician. Call 1-888-GENERAC (1-888-436-3722)
M-F 7am-6pm Central
Top Generac Electrical Supplies Experts
vince
Paul Bade
Are you a Generac Electrical Supply Expert? Answer questions, earn points and help others