Assuming you have an oil fired unit. hot and neutral wires on circ should be connected to C1 and C2 respectively. Tstat should be connected to TT which will energize circ on a call for heat and boiler will run based on limits. If you boiler is set for cold start the circ will only run on a call for heat. If you have more than on tstat/zone then you probably have either a zone control box or zone valves and transformer. If that is the case I would defer to a heating professional.
Choose two colors of the thermostat wire, and connect them to the NO and COM and connect them to the zone control board leads for the zone intended. Almost all zone valves spring return open when deenergized. So ensure the zone valve is open with the system is off. At the base of zone valve there is a set screw that needs to engage the damper valve shaft in the open position with the motor in the spring release position. Most zone valve are 90 degree moment from full open to full shut. If you have a Carrier zone valve, they go full open to full shut in 45 degrees of motion. Your open stop need to be set so the valve stops in the full stop position.
To help understand the operation of a zone system, say you have 2 zone system and zone 1 thermostat initiates a heat or cool demand. Zone 2 valves energizes and shuts and zone 1 stays open and allow air to heat/ cool zone 1. If zone 2 thermostat simultaniously initiates the same heat/cool demand, the zone 2 valve opens and both zone heat/cool. When either thermostat is satisfied the opposite zone valve closes and when both thermostat are satisfied both zone valves open.
Hope this helps you understand zone operation. The same works for higher multizone systems.
I have only seen one Honeywell thermostat that would work with a 3-wire heating system.
I would replace it with a White-Rodgers 1F80-0471. They are about $100, but they are a good thermostat, and they work well with the 3-wire zone valves.
Most other thermostats have the "Y" terminal that you need, but do not control the zone valve correctly.
Hello. Each zone in you home has one thermostat controlling one zone valve. Generally, when a thermostat is calling for heat the zone valve opens and the circulating pump comes on to move the water around that loop. If your other two zones are both working as they should and you now have a new zone valve on the third loop I would suspect that the thermostat is faulty. Regards, Joe