You valve might be bad
Check air filter is not blocked .
Testimonial: "The air filter is clean. In fact, I removed the filter to test for air obstruction. Thanks any way."
SOURCE: My Furnace does not turn on. Installed a new
Assuming the inducer fan and pressure switch are working fine, your next step is to test the voltage coming to the gas valve. There should be 4 wires going to the gas valve, one is black. This is the 24 volt power side. Unplug the molex connection at the gas valve and while the inducer is running test for 24 volts AC. If you get voltage you have a bad valve. If no voltage you have a bad circuit board. Test the safety circuit and roll-out sensors to make sure all switches are closed. Check for continuity across the switches.
SOURCE: I have a sv9500m 2674
Hello,If you cleaned the flame sensor and it is in the pilot flame,Try adding a ground wire from the pilot assembly to any close screw to boost the (pilot on) signal.Also if the valve has been sitting for a while give a tap once during (pilot on) to make sure the diaphram is just not hung up.I would hate to replace the valve and still have the same problem.