Led lights that glow when power is off?

I have replaced the three way switches, I have check the wire between the lights and switches, they are correct. I believe that this problem is caused by the source, source power, neutral a ground. I think that the ground and neutral are crossed. what do you think?

1 Answer

pawnpower

Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Master:

An expert who has achieved Level 3.

  • Master 851 Answers
  • Posted on Oct 19, 2018
 pawnpower
Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Master:

An expert who has achieved Level 3.

Joined: Oct 07, 2008
Answers
851
Questions
1
Helped
246955
Points
2332

I think you should hire a competent electrician. your question indicates you aren't qualified or competent to work on electric power, and it could cause a fire.

5 Related Answers

Anonymous

  • 883 Answers
  • Posted on Jun 03, 2007

SOURCE: Problems with Infinity Amp 611A

are you running a large ground wire directly to the battery negative terminal?

Ad

Anonymous

  • 1 Answer
  • Posted on Aug 06, 2008

SOURCE: 1990 geo metro headlight problem

hmmmm sounds like you are on the right track with the ground . with as much current as headlights pull it is possible that the intermittent open you are experiencing has to do with heat coming from an open in the wiring . i believe your best bet would be to locate a wiring diagram for your cars headlight circuit and inspect every wire in that circuit as well as one surrounding for thing like : burn marks , corrosion , places where insulation has worn off or is no longer even there ( :) ) ,and i believe you may find something . also , some cars come with a set of relays specifically for the headlights . these the headlights may be drawing extra current through the relay causing it to switch off (means headlights are bad ) , or the relay itself may have worn out over time (relay (s) may be bad ). i hope this helps you

Anonymous

  • 19 Answers
  • Posted on Jan 04, 2009

SOURCE: Connecting Leviton Decora light switch.

At the switch you have a feed wire coming in this brings in power which originates in the electric panel. You also have a feed or feeds goings out to other lts or switches, this you seem to have on the switch. instead of the closet switch loop.undo all the wires. find the only hot this is the one wire you can touch to the others and make different lts come on i reccomend getting a electric tester to do this. FInd the wire that goes to the closet lt. Once your sure put it to the side. wirenut all other wires together with the hot wire. this makes all other switches independantly hot. connect the hot to the switch and the closet lt to switch. I HOPE THIS MAKES SOME SENSE TO YOU . let me know if i can help

Anonymous

  • 3 Answers
  • Posted on Jan 24, 2009

SOURCE: ceiling fan pull chain switch replacement

Just take either one of the black wires from the switch and connect it to the group of black wires. Then take the remaining black wire from the switch and connect it to the single black wire coming into the light kit. Finally check the bulbs to be sure they're not burned out. 
Thanks and good luck

Anonymous

  • 119 Answers
  • Posted on Feb 27, 2009

SOURCE: volks wagen golf diesel tdi Nreg

Check the glow plug thermo sensor...found in the cylinder head.
Unlightly anything wrong with injector pump.
Good luck
John

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

Sir, Iam using the ZED-10FX Allen & Heath mixer. Iam not getting the 48V phanthom power and AUX out from the mixer both Green and RED LED on Phanthom power is not glowing. Iam getting the LED VU m

sOMEHOW YOU BLEW THE 48 v PHANTOM SUPPLY.
Open it up and check power board voltages.
Replace regulator circuit and check for shorts on your mic cables.
PEACE---
0helpful
1answer

PIR switches and house wiring is incompatable?

Several possibilities. First use standard light bulbs until it is working. Some of the PIR have triac outputs which need a minimum amount of current to work. CFL and LED lights can be a problem with electronic switches/dimmers.

The PIR needs electricity to operate. The black and white wire are probably power and return, there is no neutral to connect to the PIR. Unless you can get a different PIR that does not need line power to operate you are out of luck. There may be some that can cycle steal power and would work but I am not familiar with them.

I assume the three way is a three way PIR and the lights that are flickering are electronic such as LED or CFL.

If you talk to one of the people where you bought the switch they may help you free of charge.

Good Luck
1helpful
1answer

I have a goodman furnace GMP100-4 REV B..about a year ago it was not working. The fan would start but it would not ignite. We found out we need a new ignitor and it was a good quick easy fix. Now a ye

Any light flashin on the control board? If not then look for a small fuse blown on the board. See lights a flashing count them flashes

A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

If you need further help, reach me via phone at https://www.6ya.com/expert/dan_73bbd84fe1d95b61

1helpful
1answer

I have a Goodman GMP 125-5 furnace. It had a 3 light code i replaced the presure switch now it is giving me a 1 light code please help

A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
themobilian_3094.jpg

If you need further help, reach me via phone at https://www.6ya.com/expert/dan_73bbd84fe1d95b61

1helpful
1answer

Suddenly not working im not sure if there even is a pilot to be lit

Goodman have troubleshooting idiot lights on the board. Look for flashes and count em.
The flash explanations are printed on the backside of the blower cover on most models.
A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

If you need further help, reach me via phone at https://www.6ya.com/expert/dan_73bbd84fe1d95b61

0helpful
1answer

My central heating is on lockout and the burner is with red light

A sampling of various codes on a furnace

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your Goodman furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

If you need further help, reach me via phone at https://www.6ya.com/expert/dan_73bbd84fe1d95b61

0helpful
2answers

I replaced my old 3way toggle switches with the LEviton 5613 3way lighted rocker switches. Wired exactly the way the older toggle switches were wired. Switches work fine just like the older ones but one...

http://www.leviton.com/OA_HTML/ibeCCtpItmDspRte.jsp?item=4044§ion=10103&minisite=10025
The Leviton page for Leviton 5613 does not have a troubleshoot.
Manual shows simple wiring diagram.
3-way switches will not operate lights if switches are wired incorrectly.
Check your ground wire is connected.
Leviton 5613 series is illuminated.
Check that both switches have 5613 number.
Swap switches and see if problem is inside switch.
0helpful
1answer

Installing a 7 day digital wall timer

Swylite LST100 timer has 4 wires. Red, Blue, Black, White
Timer has more wires than wall switch because timer has electric clock inside. And with + series Swylite timer, it also has led bulb that needs power.

Timer can replace ordinary on-off switch
-On-off switch has 2 screws, so 2 wires (plus ground wire) connect to on-off switch
-Three of the four timer wires are used when replacing on-off switch
-Red wire is not used, it is capped off

Timer can replace 3-way switch
-Three way switch has 3 screws, so 3 wires (plus ground wire) connect to 3-way switch
-One of the screws on 3-way switch is colored dark (it is crucial to identify the wire that comes off dark screw so timer can be wired correctly)

Lets replace on-off switch see diagram
Timer black goes to Hot wire
Timer blue goes to Load (light, fan, motor)
Timer white goes to Neutral
Timer red is capped off.

How to check which wire is Hot, Neutral and Load
Switch you are replacing has 2 wires > one is Hot, the other goes to Load
Remove these two wires. Separate wires so you can test. Turn on power. Tape tester leads to wood sticks so hands are away from power. Test each wire to bare copper wire.
When tester lights up >> that is Hot wire >> please connect this wire to Timer black wire
The other wire goes to Load >> please connect this wire to Timer blue wire.
Now test for Neutral. Test Hot wire to other wires inside box. Neutral should be white. When tester lights up, that is Neutral. Please connect Timer white wire to neutral. IF YOU DO NOT have a neutral, you can connect Timer white to bare ground wire until you have time to drop a Neutral into the box.

Replace a 3-way switch see diagram
Three-way switch has 3 wires.
Identify which wire connects to Dark screw on switch >> and then please connect this wire to Timer Black wire.
Timer white wire connects to Neutral
Timer blue and red wires connect to other two wires that came off switch ... they connect to either one.
0helpful
1answer

Thinkcentre M55 8806 power on off problem

May be your computer motherboard wires connection get loose or getting moisture in wires. Or there may be some earthing problem in ur power switch. First, check the wires connection & tighten up properly. if problem persists, check the earthing by power tester. Check you RAM if it is properly tight in the jack.
0helpful
2answers

Problem with GA 8LD533

There are a few easy fixes for this, first,

Clear the CMOS (Unplug the power cord, remove the battery, and (if it's an option) move the jumper J1 (it has three pins, the jumper covers two, move it to cover the other one), unplug everything external from the motherboard apart from the PSU and power switch and speaker, replace battery, powercord, and jp1, power up - what happens?
Not finding what you are looking for?

670 views

Ask a Question

Usually answered in minutes!

Top Home Fencing Experts

ADMIN Andrew
ADMIN Andrew

Level 3 Expert

66831 Answers

ADEL AUTO DOORS
ADEL AUTO DOORS

Level 1 Expert

27 Answers

Yarik Bess
Yarik Bess

Level 2 Expert

136 Answers

Are you a Home Fencing Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...