20 Most Recent
Square D Co. HOM130 Circuit Breaker Questions & Answers
Switch stuck in trip mode
The reason why the breaker stays tripped is a result of a direct short. Unplug every electrical device plugged into an outlet in both rooms and try the breaker. If it stays on, individually start plugging in each device until the breaker trips, that is the defective device. If the breaker stays tripped, start checking wall outlets for short circuits with an ohm meter. If you did not find a short, check your hard wired lamps and appliances for shorts. If you did not find any shorts the only other problem is a shorted pair of wires in the wall or ceiling. You will need to disconnect any hard wired lamps and appliances and check for shorts between individual pairs of hot (black) and neutral (white) then hot and ground. I have a short circuit finder, but you do not need one because the technology is not perfect and you may have to manually check for shorts with a meter anyway which never lies.
My mom blew a breaker
Any circuit breaker that wont switch back on generally needs replacing. There could be a piece broken off inside that is jamming the mechanism.
I have 2 seperate circuts that keep going out then
What are you running on these two cirduits?
Is the total load more than the rated breaker?
15 amp should be protecting #14 wire. 20 amp shuld be protecting #12 wire. 30 amp #10 wire.
Add up the amps of everything you have on the line to check this. If you have Clamp Amp meter, you can measure what is going out the wire.
On second thought, if you had a clamp amp meter, you wuldn't be asking the question.
Let me know what you find out ...
a
Electrical
I am sure local code will not allow this. It needs to be hard wired from a disconnect (fusable).
Thanks
Zerko
Square D circuit breaker in a home fuse panel and I have already replaced the breaker with a new one.
i strongly recommend that you get in an electrician to investigate the problem
from your description of the amount of power required from your circuit breaker I would consider that there are to power wires from the back of that unit
one circuit to run half the points and another wire to run the rest
If only 1/2 are working, I am thinking that one of the wires at the back of the breakers is loose or come undone/broken and that will require the services of an electrician
To further explain this line of thought, each circuit in a house is designed to carry a maxim of 10 amp total (wire current capacity) so that with all outlets in operation the maximum current is 10 amps
if the required current allowed exceeds that the electricians break the numbers up so that a second circuit is employed again up to 10 amps max
if again there was a requirement that exceeded the 20 amps ( circuit breaker amp) a second circuit breaker would be installed and a 3rd circuit and so on
3/31/2017 1:55:10 PM •
Square...
Answered
on Mar 31, 2017
On a 60 FT. run using 12/2/G wire can I use a 25amp. breaker safely?
The size of the breaker that you are going to use on a circuit is predicated on the current draw of the appliance(s) you have on the circuit. Assume you have them all turned on, add up their respective amperages and , voila, you have a close approximation of the size of the breaker. If you do not know the amperage look for watts info. Divide the latter by voltage of 115 and you will arrive at the amps used.
9/25/2015 5:02:51 PM •
Square...
Answered
on Sep 25, 2015
Electrical panel dead, main and all breakers
Then, call PG&E...or your local utility company to come out and check your meter. PG&E, or your local utility company are responsible for the power up to the meter at your electrical service panel. After that, it's the electrician's responsibility...
7/1/2014 8:18:25 AM •
Square...
Answered
on Jul 01, 2014